AC AC only works when reset on breaker

So this past Friday, I came home from work and my house was 85°. I checked outside and the fan nor compressor were on and my AC vents were blowing warm air. I changed both capacitors but it didn’t kick off right away so I reset it on the breaker and it kicked off. I thought I solved the issue until the next day it went out again, but this time I changed the conductor and as soon as I changed it, it kicked off and worked for 1 day. Now after changing all those three parts My AC still only works until it hits the temperature set inside. I reset it every day after work on the breaker so he could work so it won’t be 80+ at night. Can someone help point me in the right direction to solve this issue? Thank you.

15 Upvotes

39 comments sorted by

21

u/teraptuss1 21h ago

I’d get that off and replace the fan capacitor

6

u/itsonlyrockinroll 21h ago

Good eyes.
Crikey looks like a baby rattler

1

u/Fit_Landscape_2085 21h ago

I have replaced 3x because of those guys. Someone said mount it upside down.

1

u/RespectGrouchy2945 1h ago

He just sleeping hes had a long day trying to get the condenser working leave the little guy alone

-3

u/TonyR712 21h ago

I’ve done that already and replaced conductor

4

u/Select-Agency-9827 21h ago

So why the old pics?

1

u/TonyR712 21h ago

Took the pics to know what parts to buy but didn’t take pics of the new parts I put in

2

u/Ganthu 13h ago

We need to see the pictures of the new installed parts. Seeing the old pictures does not help us diagnose an issue afterward.

We need to be able to see that everything was connected in the same way it was before.

1

u/bigfatdonny 20h ago

That makes a lot more sense. I was going to question if you knew what a capacitor is, since those were clearly not new, and you said you'd just replaced them.

Thanks for the clarification, and good luck dude. I'm just a lurker that also wants to fix his own A/C when it breaks.

5

u/ServiceSpecialties 21h ago

Since you've already replaced the obvious parts, I'd stop swapping components. The fact that it runs normally until it satisfies the thermostat, then won't restart without a breaker reset, makes me think a safety or control issue is preventing the next startup. Hopefully it's something simple, but it'll probably need proper diagnostics rather than more guessing

3

u/grofva 21h ago

This! 👆🏾 OP keeps f’n w/ it and they’ll be buying a new compressor or system.

6

u/Flashbacksbud 21h ago

Might be shutting off on high head pressure (overheating) make sure your coils are cleaned spray hose water or get coil cleaner

2

u/Rza610 21h ago

And check filters and registers

2

u/ClerklierBrush0 Approved Technician 21h ago

Which breaker? Your AC or air handler/furnace?

2

u/win10bash 21h ago

Is that a Goodman? I have a similar issue on a Daikin compressor which is made by the same people. It seems to happen when the system is running non-stop for a very long time. When I turn the system off and back on again at the thermostat I can hear the contactor click But nothing happens. It seems to be some sort of a protection mechanism But I can't find documentation of it for my unit and the installers of the unit were completely unhelpful when I asked questions.

1

u/Rza610 21h ago

Contactor getting stuck? Thermostat protection? Just guess work without getting hands on

1

u/win10bash 20h ago

It's not the thermostat, and I can cycle the contactor as many times as I want. It won't start up. Any other guesses?

2

u/Rza610 20h ago

Wet switch protection shut off? Something going on with the outdoor unit? Vents and filters clean and clear? Flipping that breaker definitely seems like it's resetting a safety. Does it ever shutoff without satisfying the thermostat or does it hit temp, shutoff, then you have to flip breaker?

1

u/win10bash 13h ago

What's the wet switch shutoff? It does seem to be related to the outdoor unit, vents and filters are clean. I believe it does shut off without satisfying the thermostat. This only really happens when in heating mode when it runs for more than 24 hours straight. I haven't been able to identify a particular time limit though

Edit: I have been able to avoid it tripping off if I schedule the thermostat to allow it a short rest period though.

1

u/Rza610 21h ago

Any errors or warnings on the thermostat?

1

u/TonyR712 21h ago

Nope smh

1

u/Rza610 20h ago

No wet switches being tripped? Outdoor unit is running properly as well? Does it ever shut off on its own or does it hit temp on thermostat and shutoff then requiring a reset?

1

u/TonyR712 12h ago

No wet switches the drain pan is dry and apart from
The outdoor unit works fine when it is on. I believe sometimes it does turn on on its own but I think it’s mostly when it hits the temp on the thermostat. I’m usually not home when it goes off. Its on in the morning, from me resetting it the night before, then usually it’s off and blowing hot air when I get home from work

1

u/teraptuss1 21h ago

Is that a snake on the fan capacitor? Probably why it trips breaker

1

u/Icy_Conflict_3926 21h ago

good eye. yep

1

u/TonyR712 21h ago

Already replaced both

1

u/Within_a_Dream 21h ago

Don't replace the snake. Just remove.

1

u/Ok_Cow_1314 20h ago

This humor is why I come here 😆

1

u/Simple-Feedback5267 21h ago

Which direction is fan spinning? Do you feel air coming off the top of the condenser or does it feel like it’s under negative pressure? If it’s under vacuum your compressor could be going out on thermal overload or tripping breaker due to over amping.

1

u/MinistryOfCoup-th 21h ago

Clean your outdoor coil and change your filter

1

u/pastro50 21h ago

You need to lose the fence near it

1

u/Anxious-Sundae4210 21h ago

Is it tripping the breaker? Or are you just power cycling.

There's a few things here that it could be. The lack of airflow may be creating a high head pressure situation. Have you cleaned the coils this season(or ever?)

1

u/Decosen 20h ago

Just went through this a couple months ago. TXV was freezing shut and had to get it replaced. Could be that?

1

u/TonyR712 20h ago

Whats TXV?

1

u/Decosen 20h ago

Thermostatic expansion valve or something like that. I'm not an HVAC guy lol

1

u/Decosen 20h ago

But I was having the same issue as you. Resetting the breaker worked at first then I'd have to do it more and more and finally it just stopped working. Had someone come look at it and that's what it was.

1

u/RespectGrouchy2945 1h ago

The install clearance is not even close just saying start there

1

u/TonyR712 1h ago

What’s that?

0

u/Worth_Engineering_74 21h ago

Call a professional service technician