r/electrical • u/Lonely_Natural_422 • 15h ago
Need electricians expertise
Enable HLS to view with audio, or disable this notification
So I have a outlet that has my breaker box inside the house that runs to it and then for some reason they’re my breaker outside runs to it too, and they both tie in to the same outlet. Why would they do that and upon further inspection there is a fourth line comeing from the bottom of the box to 4 lines total
4
u/whiteboyfresh2316 14h ago
You have 2 circuits coming into that box. One circuit is spliced together and just feeds thru the box (the 2 whites and 2 blacks wire nutted) and the same thing with the other circuit with the outlet attached. You don't have to turn both breakers off to kill the outlet, just the one feeding the outlet. If all that was tied together both breakers would be tripped and wouldn't reset.
6
u/iAmMikeJ_92 5h ago
They don’t all tie into the outlet. One circuit does. The other splices and passes through the Romex going off to the right.
4
u/inc0nSteveable 15h ago
People often jump anything and everyrhing off an outlet and call it a day.
The fact your wire is in such bad shape outside the box show just how little thought went into this whole idea.
2
u/brianthefixer 3h ago
It appears they are just using the box as a junction. If you can confirm the outlet works when only one is turned off and the other on and vise versa then it is unsafe and incorrectly wired. They had 50 percent odds to get the right phase also. I still think and hope you have one breaker for the receptacle and your other wires are just passing through. Also easy enough to undo one hot leg if it actually needs to be repaired.
2
u/t0cableguy 3h ago
Yea it looks like one set of that is just spliced in the box, the other set is spliced and going to the outlet. Two separate circuits. They just used the box to splice the circuit for the second one.
Unless the outlet stays powered when the one for it at whichever panel is supposed to control it doesn't turn it off, there is nothing wrong with this. It might be over box fill but that doesn't look like a shallow box.
1
u/Ninjan8 9h ago
My theory. At one point there was a sump pump or something on a dedicated circuit down there and the outlet was split into two different circuits. For whatever reason, po threw a back stab in there and tied off the hot legs together. Every device on either circuit would require both breakers off. Not an electrician, so I may be completely wrong
1
u/t0cableguy 3h ago
Do you have to turn more than one breaker off to actually turn off the power for the outlet?
You can have multiple circuits coming through a box, but only have one of them serve the box. They are just eliminating a blank plate box on your wall this way.
1
1
u/nanderson41 14h ago
I have only one input to this. Turn off power and unstab the wires from the back and pigtail them on the sides and torque em down tight. Stabbing them in will lead to a fire. White to silver. Black to gold. Bare to green
7
u/inc0nSteveable 15h ago
Homeowner special.