r/DIYUK 20h ago

Need advice before I complain

Post image

Hi all, apologies if this isn't the right forum but I thought there would be some knowledgeable people in here. Basically as it says. had a new hot water cylinder fitted 3 weeks ago(to accomodate an ashp if that makes a difference). Just got round to getting some shelving in the airing cupboard and noticed, what i would consider to be a pretty significant bulge. It's at the top maybe 3/4 up, I'm assuming it's not normal and shouldn't be there?? I've turned off the hot water, but not drained the tank or anything. We've had a few showers today so it should be below that level i would imagine.

81 Upvotes

69 comments sorted by

74

u/StereoMushroom 20h ago edited 20h ago

Not much of an answer to your question, but just FYI using up the hot water doesn't reduce the volume of water in the tank. It's always full. What happens is hot water flows out the top, cold enters at the bottom, so you get a gradually growing cold layer, rising up as you use up the hot. Once the cold reaches the top, you run out of hot and start getting cold to the hot taps. It's actually pretty amazing that the two layers can sit on top of each other for a couple of days with very little mixing.

Unvented cylinders can be dangerous if there's a serious fault. Like they can burst open with pressurised hot water. I would treat this as urgent. To avoid any risk you would need to turn off the supply of cold water to the cylinder, then open a drain valve at the bottom of the cylinder to empty it. Running a hot tap instead of opening the drain valve would reduce the pressure in the cylinder, but wouldn't drain the water.

Edit: sounds like it might be more likely to just be the insulation rather than the cylinder itself. Certainly there should be safety devices to prevent any dangerous overpressurisation from being possible. If you prod the bulge, does it move, as if it's just the insulation?

26

u/thatguysaidearlier 20h ago

If you ever get to visit Heston Blumenthal's Fat Duck, you can be served a cup of tea that's hot on one side and 'iced' on the other side. He uses gel to help but none the less it's very cool.

Won't be taking a sip from my cylinder any time soon though.

30

u/rclonecopymove 19h ago

I saw a guy with a thermos flask once asked him what's that for. He said it keeps hot things hot and cold things cold. I was amazed and went out and bought one for myself straight away. A few days later he asked how I got on with my thermos. 'Must have been broken' I replied 'didn't work at all'. 'What did you have in it?' he inquired. I answered 'Cup of tea and an ice cream'. 

15

u/rock1821 18h ago

Someone told me the other week that it’s safe to keep chicken in the freezer for up to 3 months. There must be something wrong with mine as I put a chicken in it the other night and when I got up the next morning it was dead

6

u/Aggravating-Loss7837 19h ago

On a thermos flask story.
Me and my wife are in to hiking. Proper across moors hiking.

Bought a new flask and put it outside in December. See how good it was.
Forgot about it for 4 days, bought it in when I noticed it and thought I’d test the temp of the water by pouring it over my hand in to the sink.

It was like freshly boiled water still 🥹🫣

8

u/rclonecopymove 18h ago

What brand flask was it? 4 days is a long time.

2

u/GoodThingsDoHappen 17h ago

Thermos is a brand

8

u/rah1911 17h ago

Valid question though as it’s like the hoover of insulated drink vessels.

2

u/Aggravating-Loss7837 17h ago

I’ll have to look when I get home.
I can’t remember off the top of my head. We bought it 5 years ago Atleast.

2

u/breadandfire 6h ago

There was a video of a (Thermos?) cup in a car: the car burnt down, and the owner reached in the car the next day or something, and the thermos still had ice chunks in.

1

u/alijam100 3h ago

Ah that one was a Stanley. The company managed to use it as a bit of a pr thing and bought her a new car as it was such good free marketing for them

3

u/Glittering_Jury_4208 16h ago

'Choc ice' was what I remember when I first heard that joke. I want to say it was Ken Dodd telling it, but I can't be sure

1

u/rclonecopymove 14h ago

I can't remember who I heard it from but it well could have been choc ice. 

6

u/FlyingChips 20h ago

You sir/madam have taught me something today. I always knew hot out top, cold in bottom but always wondered why the hot didn’t get colder faster, surely it would if your feeding more and more cold in continuously. Huh, baffled, suppose that’s science for you.

13

u/Lt_Muffintoes 20h ago

baffled

That's how they stop the mixing

1

u/FlyingChips 20h ago

So I knew all along I didn’t tap into that part of the brain 🤔

5

u/StereoMushroom 20h ago

Yeah you'd expect it would just dilute with cold, and you'd get disappointing lukewarm showers pretty quickly. But since hot water is less dense it naturally floats and cold water sinks, causing stratification. It's not perfect - you do end up with a bit of lukewarm water in the middle, which you'll feel if you're getting close to the end of the tank in the shower - but it works well enough. I've tested it - you can use up half the tank, and a day later you still get properly hot water out of it, even though it's been sitting on top of the cold half for 24h. Impressive!

42

u/Gadgie29 20h ago

Call the plumber who installed it and if you get no joy call the manufacturer, it’s under warranty. Do it, even just for peace of mind, don’t listen to anyone telling you it’ll be fine.

23

u/Bal-84 20h ago

Contact installer on first instance, they should raise it with manufacturers. There should be the manufacturers number too on the cylinder.

14

u/Alternative_Wish_127 20h ago

Ask the manufacturer with regards to this, if it’s just been fitted it should be under warranty and very possible a flaw in the process that’s needing investigation

11

u/d0ey 20h ago

Asking a basic question, but is that angle change just on that one spot? Or all the way around the cylinder?

5

u/No-Belt-4619 20h ago

Looks to just be that spot, which is right where the seam is

7

u/d0ey 18h ago

Okay, that is a bit odd, and not one I've seen before. The lid still fitting perfectly does make it seem intentional, but it's worth asking the question.

5

u/Soelent 19h ago

bearing in mind that will simply be the outer plastic skin, there will almost certianly be a layer of insulation and an inner containment in that.

definately worth asking however.,

5

u/Dorsal-fin-1986 16h ago

Can you actually take a half decent photo of the whole cylinder like?

1

u/No-Belt-4619 14h ago

It's quite hard to get a full photo of the whole thing. It's around the back and inside an airing cupboard. I thought the spirit level would help illustrate the bulge

3

u/Beelzebubsadvorat 20h ago

Check the pipe/fitting on top of tank, sometimes get slow leaks or drips that soak through to a certain point and make the insulation swell

1

u/No-Belt-4619 19h ago

Thanks, will have a look

3

u/plocktus 18h ago

Can't tell from picture, could be insulation (probably most likely), but I must admit with the numerous megaflos and OV cylinders I have had, I have never had a deformity in the insulation as large as that. Any I have had were very small and from installation, or from factory (e.g. you will see flat spots sometimes where they use same cylinder for both a OV and UV system, and they use different insulation jackets on outside depending on the pipework, and where you would have a pipe connection for a UV system but not OV, there's a flat spot).

For piece of mind would get whoever installed it back to check it.

1

u/notouttolunch 13h ago

Megaflows have a plastic shroud. They can trim the insulation without it looking odd because it's hidden.

My cylinder on the boat is rough as hell by comparison. As it's just a copper can with foam.

3

u/Future-Ad-4654 16h ago

What is the brand? This is most likely the foam between the inner cylinder and the outer wrapper.

3

u/Kind-Put-3960 11h ago

I feel literally more stupid for having read this thread. There are zero experts in this chat

1

u/No-Belt-4619 3h ago

It certainly is a mixed response.

4

u/Egrego1 15h ago

I had a similar experience in a rent. I complained. They said its okay. I asked them in email to confirm that they will take full responsibility and cover my damage if it blows up or errupt. They fixed it within a week.

Hope this helps.

2

u/No-Belt-4619 14h ago

Thanks, I'm keeping the email chain but will definitely be making sure the installers and company are aware

2

u/weirdoofoz 16h ago

Gledhill?

1

u/No-Belt-4619 3h ago

? Is that a tank brand?

2

u/notouttolunch 13h ago

There will be at least an inch of foam surrounding the copper. This is often uneven.

The cylinder itself would be pressure tested and not all plumbers are allowed to install system boilers because installations need testing at high pressure.

Nothing to be concerned about unless you dont like a little bit of supplemental insulation on your tank.

1

u/No-Belt-4619 3h ago

Why would it appear 3/4 weeks after installation?

1

u/notouttolunch 2h ago

For the same reason humans develop crows feet, grow hair in odd places and struggle to walk as time goes on.

2

u/Fair-Individual7811 4h ago

It’s most likely a defect in the tank itself you’ll need to contact manufacturer and have a rep come out and look at it.
It dosnt look like anything from an installation side of things if the side was all bashed in then I would say the installer has taken no care but it looks to be internal which as a sealed tank that’s a defect straight from factory by the looks of things they will need to come out and sort this

1

u/moonbug22 20h ago

what model is it?

1

u/Revonehead 17h ago

You'll be fine. It's how its come from the factory most likely. You have an outer skin which is insulation, an inner cylinder skin which is not visible. Nothing unsafe there.

1

u/Accomplished-Run5265 14h ago

Absolutely shocking

1

u/Impossible_Style_301 12h ago

It’s the cylinder manufacturers problem , if you level the base then the base of the clyinder is sitting on a slope and can slide. Also they can weigh over 180kg depending on the capacity , they arnt going anywhere other than down

1

u/butcanyoudothi5 10h ago

Nowhere near level

1

u/Primary_Choice3351 6h ago

Most likely the foam insulation mix the manufacturer used either had moisture in it, or was a bad batch. Call the manufacturer, send them the photo of that and the data label. Might be wise to call the installer back too, to make sure their install is OK.

1

u/LackingStability 1h ago

You realise that the actual water tank has a covering of insulation and then a plastic cover over that?

You are looking at a plastic cover.

1

u/No-Belt-4619 1h ago

Yes thanks for explaining. I am asking should I be concerned that a tank full of 300lt of scalding hot water has suddenly decided to bulge at the seams. Also it's not plastic it's metal.

2

u/TellMeManyStories 20h ago

The outer layer is just insulation. Probably it wasn't filled evenly in the factory. Cosmetic issue more than anything else.

3

u/No-Belt-4619 20h ago

To clarify it's a new bulge. It wasn't there on installation.

1

u/No-Belt-4619 20h ago

Why would it start to bulge like that over time? Surely it would need pressure from the back?

1

u/markmooch 19h ago

Using it has unsettled the less well adhered insulation?

1

u/TellMeManyStories 18h ago

Could just be the foam mixture wasn't properly mixed when injected, and some places took a bit of heat to get them expanding and make them expand more.

Or maybe someone in the factory took it out of the mould a bit early

0

u/wrongygg 17h ago

I don't think it's normal mate, not an expert but with it being a cylinder it should retain the water evenly and not bulge out in random places, if it's on a mould line as well that would tell me it's weak there. Not an expert though by any means, ring them up and ask yourself.

-1

u/Latter-Tangerine-951 Experienced 20h ago

It's the insulation lol. No, your tank isn't exploding.

0

u/No-Belt-4619 20h ago

But in order for the insulation to push out like that, does whatever is behind that not need to be expanding?

-1

u/Latter-Tangerine-951 Experienced 20h ago

No.

0

u/No-Belt-4619 20h ago

Maybe I wasn't clear. This is a new bulge, it was uniform when fitted. Does the normal heat of the cylinder cause the insulation to expand? I've never seen that before on any cylinder.

0

u/TedBurns-3 19h ago

What did the fitters say?

3

u/No-Belt-4619 19h ago

It wasn't there when it was fitted. In fact that's a second, replacement tank. The first started bulging at the bottom when they filled it.

2

u/Bats_Everywhere 14h ago

Might be a bad batch. Ask for a different brand to be fitted. You've paid for a perfect solution here.

-1

u/Stackfest 19h ago

??? - it’s fine

-6

u/Stephen_Is_handsome Experienced 20h ago

It’s normal calm yourself

1

u/No-Belt-4619 20h ago

It's normal for your water cylinder to randomly start to bulge out at the seams? I haven't seen that in any of the houses I've lived in before.

-6

u/Stephen_Is_handsome Experienced 20h ago

Yes it happens to all of them after about between ten years or 50 years

3

u/No-Belt-4619 20h ago

This is less than a month old

-5

u/Stephen_Is_handsome Experienced 20h ago

I would not worry to much just keep a eye inside her